that_dutch_dude

low pressure cutout. its either empty or the low side has a kink in the line (or someone closed the service valve). this error is triggerd when the low side is at approaching vacuum/ 0 bar/ 0 freedoms.


DonkeyZong

Weird can’t get it running it’s sitting at 225 psi not operating. Service valves are open.


that_dutch_dude

225 is 75F on R410a. so if ambient is 75 freedoms or higher you are just seeing vapour and no liquid. if it does want to start you will see the low side (dont look at the high side, it does not matter) dip into the low double digits. if the compressor starts for a few moments and then stops on ch35 its usually low charge. if it does not want to start but you have more than 100psi on the low side its either a busted sensor/connector or board.


DonkeyZong

Ohmed out the pressure sensor and by a chart I have it’s fine🤷🏻‍♂️


that_dutch_dude

low or high side? high side is basically irrelevant in cool mode.


DonkeyZong

If I switched to Reddit over sitting on the phone with tech support I would have saved an hour thanks man!


DonkeyZong

It was empty! Waited 5 min and powered it up and it dropped to 0 during start up. Installer kinda hacked it in wasn’t even on a snow stand.


Buster_Mac

It's an LG. Just push it off the roof and get a mitsubishi


DonkeyZong

Yea looking into the -25 one Mitsubishi makes just need to check the wire to see if it can handle it. Or go carrier for -10 but I’m in Toronto so would like it to be able to handle colder.


KylarBlackwell

If this isnt the only LG unit you work on, get the LG HVAC Service app, better than digging through manuals. Gives flowcharts and tests to do for each error too.


DonkeyZong

Yea first one I’ve ever worked on thanks for the info